I'm getting all the facility surveys conducted on all of these buildings that have major problems with ADA compliance. Note that BEP operators and MCB and MRS have operations in these public buildings now 20 years out of compliance.
In addition DTMB does have responsabilities over leased facilities to ensure accessability. They know that to in other documents.
Joe
Americans with Disabilities Act
Michigan ADA Summary
for Department of Management and Budget
Owned Properties
File No. 071/06401.FAR
Summary Conducted By:
Integrated Architecture Capital Area Center for Independent Living
Table of Contents Page 1
Americans with Disabilities Act
Michigan ADA Summary
for Department of Management and Budget
Owned Properties
File No. 071/06401.FAR
• Table of Contents
• DMB Project Statement
• DMB Request for Proposal
• DMB Owned Buildings List
• Maps
• Blank Copy of Building Audit Checklist
• ADA Compliance Unit Costs
• Building Summaries:
Building Number Building Name
1 Allegan Plaza
2 Allegan Ramp
3 Constitution Hall
4 Grand Tower
5 Hall of Justice
6 Hannah Building
7 Joint Operations Center
8 Lewis Cass Building
9 Lottery Building
10 Michigan Library and Historical Center
11 Murray D. VanWagoner Building
12 Ottawa Building
13 Ottawa Ramp
14 Richard H. Austin Building
15 Romney Building
16 Roosevelt Ramp
17 Stevens T. Mason Building
18 Williams Building
19 Joint Lab Building
20 Record Center (Building 20 was sold during the course of the audit and no
report was prepared.)
21 Energy Center
22 General Office Building
23 General Service Building
24 Highway Central Warehouse
25 MDOT Construction and Technology
26 MDOT Photo Lab
27 MSP Forensics Lab
28 MSP Hazardous Material Training
Table of Contents Page 2
29 Operations Center
30 Police Training Academy
31 Secretary of State
32 State Police Fist District Headquarters
33 Vehicle and Travel Services
34 Escanaba Building
35 Flint Ramp
36 Flint State Office Building
37 Grand Rapids Building
38 Grand Rapids Ramp
39 Jackson Building
40 Jerome T. Hart Building
41 Traverse City State Office Building
building #34
(escanaba)
buildings #35
& #36 (flint)
N
building #41
(traverse city)
buildings #37 & #38
(grand rapids)
building #40
(saginaw)
building #39
(jackson)
buildings #1–
#20 (lansing)
buildings #21–#33
(dimondale)
State Owned Buildings Keyplan
N
building #19
building #4
INTERSTATE 496
GRAND RIVER AVENUE
building #5
building #10
building #7
building #16
building #15
building #9
building #8
building #3
allegan plaza
buildings #1, #2, #6, #11,
#12, #13, #14, #17 & #18
MARTIN LUTHER
KING JR
BOULEBARD
MICHIGAN AVENUE
CEDAR STREET
Lansing
N
building #32
building #23
building #22
building #28
building #27
building #26
building #24
building #21
building #29
building #31
building #33
INTERSTATE 96
building #30
building #25
LANSING ROAD
CANAL ROAD
INTERSTATE 69
Dimondale
N
building #34
LINCOLN ROAD
LUDINGTON STREET
LAKE SHORE DRIVE
Escanaba
Flint
N
buildings #35 & #36 INTERSTATE 475
MARTIN LUTHER KING AVENUE
kEARSLEY STREET
INTERSTATE 69
N
INTERSTATE 196
buildings #37 & #38
US 131
MICHIGAN AVENUE
DIVISION AVENUE
Grand Rapids
MONROE AVENUE
COLLEGE AVENUE
N
INTERSTATE 94
US 127
LOUIS B. GLICK
HIGHWAY
FRANCIS STREET
Jackson
GANSON STREET
MICHIGAN AVENUE building #39
N
building #40
INTERSTATE 675
LAPEER AVENUE
WASHINGTON AVENUE
Saginaw
GENESEE AVENUE
N
building #41
ELMWOOD AVENUE
DIVISION STREET / US 31
Traverse City
8TH STREET
SILVER LAKE ROAD
Americans with Disabilities Act
Michigan ADA Summary
for Department of Management and Budget
Owned Properties
File No. 071/06401.FAR
Building Name
Address
Survey Building #
Summary Conducted By:
Integrated Architecture Capital Area Center for Independent Living
Date of Building Audit:
Date of Summary:
Building Name – Survey Building # Page 2
ADA Summary
for Department of Management and Budget Owned Properties
Priority One – Access to Building
People with disabilities should be able to access a public building from many forms of transportation.
Approaching the site from public transportation should be moderately convenient and safe. Parking lots
and street parking should also have ample accessible spaces, plus an accessible route to the main
entrance.
A. Access to Public Transportation
A.1. Accessible from public transportation?
Distance to bus stop:
Type of bus:
B. Access to Building by Vehicular Drop-off from Street
B.1. Accessible vehicular drop-off (van or passenger vehicle)?
Distance from main entry:
B.2. Is the drop-off area at least 20 feet long and 5’-0” wide?
B.3. Is the drop-off area relatively flat (1:50 or 2% slope)?
B.4. Is a curb ramp provided at the vehicle drop-off area?
B.5. If a curb ramp is provided, is the slope of the ramp no more than 1:12?
Approximate slope of ramp:
B.6. Is the width of the ramp 36 inches or more, not including the flares?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 3
B.7. Does the curb ramp have vision impaired grooves?
C. Accessible Parking
C.1. Are an adequate number of accessible parking spaces available (8 feet wide with 5 foot
access aisle)? Refer to requirements for spaces below.
Parking Requirements: Total Spaces Accessible
1 to 25 1 space
26 to 50 2 spaces
51 to 75 3 spaces
76 to 100 4 spaces
Number of accessible spaces on site:
C.2.A. Is there a van accessible parking space (8 feet wide with minimum 8 foot aisle)?
C.2.B. How many van accessible spaces are there?
Number of spaces:
C.3. If accessible parking is located in an adjacent garage, does it have vertical clearance of 8’-2”
to the parking space?
C.4. Are all the accessible parking spaces and access aisles relatively level (1:50) in all
directions?
C.5. Are all the accessible parking spaces marked with a sign with the “symbol of accessibility”
that is visible when a vehicle is parked in the space?
C.6. Is the pavement at the parking properly striped and readable?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 4
C.7. Is an accessible route provided from the designated parking area to the main sidewalk (must
be 36 inches wide and have proper slope, maximum of 1:12)?
D. Visible Building Entry
D.1. Is the building signage visible from the street?
D.2. Is the building name visibly labeled at the main entry?
D.3 Is the building name tactilely labeled at the main entry?
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 5
Priority Two – Accessible Entry
A building must provide one accessible entry approach to the building, preferably the main entry. This
entry must allow people who use crutches, canes, walkers, scooters or wheelchairs to use it.
Describe entry location at building:
A. Accessible Path to Entry
A.1. Is there a route from the street or parking area that does not require stairs?
A.2. Is the route of travel stable, firm and slip resistant?
A.3. Is the travel path at least 36 inches wide?
A.4. Is the path free from any protrusions or objects that a person with a cane can not detect?
(Objects that protrude more than 4 inches must be above 80 inches.)
A.5. Is a ramp or lift provided to a ramp to gain entry to the building?
A.6. Ramps
A.6.1. Are the slopes of the ramps 1:12 or less?
Approx. slope of ramp
A.6.2. Are handrails provided at 34 inches to 38 inches A.F.F. (only required if the ramp is
6’-0” or longer)?
A.6.3. Is the width between rails 36 inches or more?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 6
A.6.4. Is the surface slip resistant?
A.6.5. If a ramp is more than 30 feet long, is a level landing at least 60 inches long provided
at every 30 feet of horizontal length?
Note: if the running slope is less than 1:16 but more than 1:20, each ramp segment
may be up to 40 feet long followed by a level landing.
A.6.6. Is there a level landing, at least 60 inches by 60 inches, when a ramp changes
direction?
A.6.7. Does the ramp have a vertical edge protection?
A.7. Accessibility Lift
A.7.1. Is the lift in working order?
A.7.2. What is the approximate age of the lift? Years
A.7.3. What brand is it?
A.7.4. Is the lift protected in inclement weather?
A.8. If the main entry is not accessible, is the location of the alternate entry clearly marked with a
sign?
A.9. If there are stairs, do they have contrasting material at the leading edge of the steps?
YES
NO
YES
NO
N/A
YES
NO
YES
NO
YES
NO
N/A
YES
NO
YES
NO
N/A
YES
NO
N/A
Building Name – Survey Building # Page 7
B. Doorways and Vestibules
B.1. Does the entrance door have at least 32 inches clear opening (for a double door, at least one
32 inch leaf)?
Actual size: inches
B.2.A. Does the door have an automatic or power operated mechanism?
Location of power mechanism: feet
B.2.B. Is the path of travel accessible?
B.3. On the latch, pull side of the door, is there at least 18 inches clearance provided if the door is
not automatic or power operated?
B.4. Is the hardware (e.g., lever, pull, and panic bar) usable with one hand without tight grasping,
pinching, or twisting of the wrist?
B.5. Is the door hardware within 48 inches of the floor?
B.6. If there is not a power operated door, can the door be operated without too much force?
Pull force: lbs.
B.7. If the door has a closer, does it take at least 3 seconds to close?
Actual time open: seconds
B.7.1. Is there enough time?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 8
B.8. Are all threshold edges ¼” high or less, or if beveled edge, no more than ¾” high?
Number of doors that are non-conforming:
B.9. If an entry has a vestibule, is there a 30 inch by 48 inch clear floor space inside the vestibule
where a wheelchair or scooter user can be outside the swing of a hinged door?
B.10. If there is a vestibule, are doors spaced 7’-0” or more apart? (Verify space between swing
end of door to be a minimum of 48” clear).
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 9
Priority Three – Access to Programs, Services and Activities
Ideally, the main level of a building should allow people with disabilities to enter and use all public spaces.
>From the front door to all locations that serve the public, the route should meet ADA standards.
Building Level:
A. Accessibility to Rooms and Spaces
A.1. Does the accessible entrance provide direct access to the main floor, lobby, or elevator?
A.2. Are all public spaces on the main level on an accessible route of travel?
A.3. Is the accessible route to all public spaces at least 36 inches wide?
A.4. Is there a 5 foot circle or T-shaped space at each horizontal corridor to reverse direction in a
wheelchair?
A.5. Is the flooring throughout the main level slip resistant material, a low pile or tight woven
carpet, or without major level changes of more than 1/4 inch?
Remarks:
A.6. In the circulation path through the public spaces, are obstacles cane detectable (located
within 27 inches of the floor or higher than 80 inches, or protruding less than 4 inches from
the wall)?
Remarks:
B. Doors
B.1. Do doors into each public space have at least a 32 inch clear opening?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 10
B.2. On the pull side of doors, next to the handle, is there at least 18 inches of clear wall space so
that a person using a wheelchair or crutches can get near to open the door?
B.3. Can doors be opened without too much force (5 lbf maximum for interior doors)?
B.4. Are door handles 48 inches high or less and operable with a closed fist?
B.5. Are all threshold edges ¼ inch high or less, or if beveled edge, no more than ¾ inch high?
B.6. Is the door hardware throughout up to date with lever hardware?
If not, how many doors have hardware that needs to be replaced?
C. Emergency Egress
C.1. If emergency systems are provided, do they have both flashing lights and audible signals?
C.2. Is an emergency evacuation plan visible and accessible?
Remarks:
C.3. Is an evacuation chair available?
C.4. Is there an area of refuge designated?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 11
D. Signage
D.1. If provided, do signs and room numbers designating permanent rooms and spaces where
goods and services are provided comply with the appropriate requirements for such signage?
D.2. Are signs and information boards mounted with centerline 60 inches from floor?
D.3. Mounted on wall adjacent to latch side of door, or as close as possible?
D.4. Raised characters, sized between 5/8 and 2 inches high, with high contrast (for room
numbers, rest rooms, exits)?
D.5. Is there Brailled text of the same information?
D.6. If pictogram is used, is it accompanied by raised characters and Braille?
E. Vertical Circulation
E.1. Are there ramps, lifts, or elevators to all public levels?
E.2. On each level, if there are stairs between the entrance and/or elevator and essential public
areas, is there an accessible alternate route?
E.3. Do treads have a non-slip surface?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
N/A (if checked, skip to E.7)
YES
NO
Building Name – Survey Building # Page 12
E.4. Do the treads at the stair have a high contrasting color change?
E.5. Do stairs have continuous rails on both sides, with extensions beyond the top and bottom
stairs?
E.6. At all open stair locations, are the undersides of the stairs enclosed or protected with a cane
detectable barrier?
E.7. Is an elevator provided to each public level?
E.8. Are raised letters and Braille characters used to identify each floor call button and each
control?
E.9. Are the centerlines of the call buttons mounted 42 inches above the floor?
E.10. Does the floor area of the elevator car have space to enter, reach the controls, and exit?
E.11. Can the elevator be called and operated automatically without using a special key or having
to turn on the elevator from a remote location?
E.12. Are the highest floor control buttons mounted no more than 54 inches above the floor for a
side reach or 48 inches for forward reach?
E.13. Are signs mounted on both sides of the elevator hoist way door opening (for each elevator
and at each floor) that designates the floor with 2 inch minimum height raised letters and
Braille characters centered at 60 inches above floor.
YES
NO
YES
NO
YES
NO
N/A
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 13
E.14. Is the elevator equipped with audible tones or bells or verbal annunciators that announce
each floor as it is passed?
E.15. If a wheelchair lift is provided, is it in operation?
E.16. Is the change in level from the floor to the lift surface ramped or beveled?
E.17. Is there at least a 30 inch by 48 inch clear floor space on the wheelchair lift?
E.18. Does the lift allow a person using a mobility device unassisted entry?
E.19. Are the controls and operating mechanisms mounted no more than 54 inches above the floor
for a side reach or 48 inches for a forward reach?
E.20. Where a ramp is provided, is the slope no greater than 1:12?
Note: For existing ramps, the slope may be 1:10 for a 6 inch rise and 1:8 for a 3 inch rise in
special circumstances.
E.21. Are handrails installed on both sides of each ramp segment?
E.22. Is the ramp width, measured between handrails, at least 36 inches?
E.23. Are the handrails mounted 34 to 38 inches above the ramp surface?
YES
NO
YES
NO
N/A (if checked, skip to E.20)
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
N/A (if checked, skip to F. Restrooms)
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 14
E.24. If a ramp is longer than 30 feet, is a level landing at least 60 inches long provided every 30
feet?
E.25. Does the ramp have a level landing that is at least 60 inches long at the top and bottom of
each ramp section or where the ramp changes direction?
E.26. If the ramp or landing has a vertical drop-off on either side of the ramp, is edge protection
provided?
F. Restrooms
When restrooms are provided to the public, they must be accessible at each level for all disabilities.
Level:
Type:
Location on floor:
Number of stalls:
Number of accessible:
Number of accessible urinals:
F.1. If a sign is provided at the toilet room entrance (e.g. Men, Women, Unisex), is a sign
with raised characters and Braille mounted on the wall adjacent to the latch?
F.2. Does the door to the toilet room provide a 32 inch clear passage width when the door is
90 degrees?
F.3. Inside the toilet room, is there an area where a person who uses a wheelchair or other
mobility device can turn around – either at least 60 inch diameter circle or a T-shaped turn
area?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 15
F.4. If lavatories are provided, does at least one have at least a 29 inch high clearance under
the front apron with the top of the rim no more than 34 inches above the floor?
F.5. Are the drain and hot water pipes for this lavatory insulated or otherwise configured to protect
against contact?
F.6. Does this lavatory have controls that operate easily with one hand without tight grasping,
pinching, or twisting of the wrist?
F.7. If mirrors are provided, is the bottom of the reflecting surface for the mirror at this lavatory no
higher than 40 inches above the floor or is a full length mirror provided?
F.8. For at least one of each type of dispenser, receptacle, or equipment, is there a clear floor
space at least 30 inches wide by 48 inches long adjacent to the control or dispenser
(positioned either parallel to the control or dispenser or in front of it)?
F.9. Is the operating control (switch, lever, button, or pull) of at least one of each type of dispenser
or built-in equipment no higher than 54” above the floor (if there is clear floor space for a
parallel approach) or 48 inches (if there is clear floor space for a front approach)?
F.10. Are all built-in dispensers, receptacles, or equipment mounted so the front does not extend
more than 4 inches from the wall if the bottom edge is between 27 inches and 80 inches
above the floor?
F.11 Is at least one wide toilet stall provided with an out swinging door, side and rear grab bars,
and clear space next to the toilet?
F.12. Is the toilet stall at least 60 inches wide and 56 inches deep (wall mounted toiled) or 59
inches deep (floor mounted toilet)?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 16
F.13. Is the centerline of the toilet 18 inches from the adjacent side wall?
If NO, what is the actual dimension?
F.14. Is the top of the toilet seat 17 inches to 19 inches above the floor?
F.15. Is the flush valve located on the wide side adjacent to the lavatory or is an automatic flush
valve provided?
F.16. Is a horizontal grab bar at least 40 inches long securely mounted on the adjacent side wall 33
to 36 inches above the floor with one end no more than 12 inches from the back wall 33 to 36
inches above the floor?
F.17. Is a second horizontal grab bar at least 36 inches long securely mounted on the back wall
with one end no more than 6 inches from the side wall 33 to 36 inches above the floor?
F.18. Is the door to the toilet stall located diagonally opposite, not directly in front of, the toilet or on
the opposite side wall from the wall with the long grab bar?
F.19. Unless the wide stall is located at the end of a row of toilet stalls, does the door to this wider
stall swing out?
F.20. If there are 6 or more stalls in the restroom, is one of those stalls (in addition to the wider stall
noted above) exactly 36 inches wide with an out-swinging stall door that provides at least 32
inches of clear width?
F.21. Does this 36 inch wide stall have horizontal grab bars on both of the side partitions that are at
least 36 inches long and 33 to 36 inches above the floor?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
N/A (if checked, skip to F.23)
YES
NO
Building Name – Survey Building # Page 17
F.22. Is the surface of the toilet seat in this 36 inch wide stall 17 to 19 inches above the floor?
F.23. If a coat hook is provided, is it mounted no higher than 54 inches above the floor for a side
approach or 48 inches above the floor for a front approach?
F.24. Is the door hardware easy to operate without tight grasping pinching or twisting of the wrist?
Remarks:
G. Ancillary Amenities
G.1. Telephones
G.1.1. If at least one public telephone or one bank of telephones is provided, does at least
one of each type of telephone (e.g. pay telephone, intercom telephone, other
telephone) have the following?
G.1.2. For a side approach (clear floor space at least 30 inches long by 48 inches wide), is
the coin slot no higher than 54 inches above the floor?
G.1.3. For a font approach (where clear floor space at least 30 inches wide by 48 inches
long), is the coin slot no higher than 48 inches above the floor?
G.1.4. Does the phone have volume controls?
G.1.5. Is there a sign at each pay phone or pay phone bank for the shelter directing people
to the nearest TTY?
YES
NO
YES
NO
YES
NO
YES
NO
N/A (if checked, skip to G.2)
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 18
G.2. Drinking Fountains
Number of accessible:
Number of standard:
G.2.1. If the drinking fountain is a wall-mounted unit, is there clear floor space at least 30
inches wide (36 inches if it is in an alcove) by 48 inches long in front of the drinking
fountain and at least 27 inches high under the fountain so that a person using a
wheelchair can get close to the spout and controls?
G.2.2. Is a standard height drinking fountain available also (36 inches high)?
G.2.3. If the drinking fountain is a floor mounted unit, is there clear floor space at least 30
inches long by 48 inches wide (60 inches if it is in an alcove) for a side approach to
the drinking fountain so that a person using a wheelchair can get close to the spout
and controls even though the fountain has no clear space under it?
G.2.4. Is the top of the spout no higher than 36 inches above the floor and at the front of the
fountain or water cooler?
G.2.5. Does the water rise high enough to be accessible?
G.2.6. Are the controls on or near the front of the unit and do they operate with one hand
without tight grasping, pinching, or twisting of the wrist?
G.2.7. Does the drinking fountain have a Dixie cup dispenser?
G.2.8. Is the drinking fountain recessed so that it does not hinder people who are blind or
have low vision and use a cane (protrudes 4” or less)?
YES
NO
N/A
YES
NO
YES
NO
N/A
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 19
G.2.9. Does the drinking fountain have proper tactile signage?
H. Signage
H.1. If mounted above 80 inches, do signs have letters at least 3 inches high, with high contrast,
and non-glare finish?
H.2. Do directional and informational signs comply with legibility requirements? (Temporary signs
need not comply.)
H.3. Are the bulletin boards and informational signs hung at 60 inches to the centerline of the
sign?
I. Alarms
I.1. Does the facility provide an emergency warning system?
I.2. Is it an audible alarm?
I.3. Is it a visual alarm?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 20
Priority Four – Other Public Spaces
People with disabilities should have access to all public areas of a building. Verify that each public room
has an accessible route and is flexible for all users.
A. Conference Rooms
Location in building:
A.1. Is the accessible route to each conference room 36 inches wide?
A.2. Does the door to each conference room have at least a 32 inch clear opening?
A.3. Once inside of each conference room, are the table and chairs able to accommodate a
person in a wheelchair or scooter?
Remarks:
A.4. Are audio devices or loop systems available?
A.5. Does the hardware to the room have the proper lever handle?
Remarks:
B. Auditoriums
Location and other remarks:
B.1. Is the accessible route to the auditorium 36 inches wide?
B.2. Does the door to the auditorium have at least a 32 inch clear opening?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 21
B.3. Once inside the auditorium, is there an accessible route to a wheelchair viewing area?
B.4. Is the path free from any protrusions or objects that a person with a cane can not detect?
(Objects that protrude more than 4 inches must be above 80 inches.)
B.5. How many seats are in the auditorium?
B.6. If the seating capacity is above 300, is there more than one location for wheelchairs?
B.7. How many wheelchair accessible spaces are there (33 inch wide platform)?
B.8. Is there access to performing area, stage, and podium?
Describe non-accessible space:
B.9. Is there access to backstage area: lockers, dressing rooms, and bathrooms?
Describe non-accessible space:
B.10. Is an assistive listening system (ALS) available?
B.11. Is it a fixed system?
B.12. Is the assistive listening system equipment properly located with signage?
C. Café/Dining
Describe location and type of food service:
C.1. Is the accessible route to the café 36 inches wide?
YES
NO
YES
NO
YES
NO
N/A
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 22
C.2. Does the door to the café have at least a 32 inch clear opening?
C.3. Once inside the café, is there ample seating for persons in a scooter or wheelchair?
C.4. Are the counters for service at a 34 inch level for proper access?
C.5. Are the tops of tables or dining counters between 28 and 34 inches high?
C.6. Are knee spaces at accessible tables at least 27 inches high, 30 inches wide, and 19 inches
deep?
D. Convenience Store
Describe location and type:
D.1. Is the entry to the store accessible?
D.2. Does the store have 36 inch wide aisles?
D.3. Is the service counter accessible at 34 inches?
E. Vending
Describe location and type:
E.1. Is the entry to the vending area accessible?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Building Name – Survey Building # Page 23
F. Mail Service
Describe location and type:
F.1. If there is mail service in the building is it accessible?
G. Outdoor Eating Area
Describe location and type:
G.1. If there is an outdoor eating area is it accessible?
H. Displays (Museum or Historical)
H.1. Are displays within the building at a height that is visually viewable to someone in a
wheelchair?
H.2. Do the displays have signage that can be used by the visually impaired?
H.3. Do the displays have audible devices that can be used by the hearing impaired?
I. Service Animals
I.1. Is there a relief area for service animals?
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
YES
NO
Integrated Architecture
4 0 9 0 L a k e D r i v e G r a n d R a p i d s M i c h i g a n 4 9 5 4 6 t e l 6 1 6 . 5 7 4 . 0 2 2 0 f a x 6 1 6 . 5 7 4 . 0 9 5 3 w w w . i n t a r
c h . c o m
ADA COMPLIANCE UNIT COSTS
Date: 12 January 2008
Project: State of Michigan ADA Survey
IA Project No.: 280316
ADA Unit Cost – Material only unless noted otherwise:
1. $35 each for ADA room sign with Braille.
2. $85 each for replacing door hardware with lever type.
3. $60 each for plumbing wrap on a sink.
4. $5 each for painting edge on a step lead edge.
5. $220 each for graphic location sign.
6. $800 each for lowering counter for ADA compliance at one desk area.
7. $35 each for Braille sign at each elevator floor.
8. $250 each for outdoor sign No Public Space.
9. $80 each for painting one ADA parking space.
10. $350 each for adding grooved strips in walk at curb.
11. $400 each for reworking door threshold flush with floor.
12. $180 each for exterior sign ADA Access To Building.
13. $80 each for relocating Fire Pull station.
14. $6,000 to $8,000 per elevator for adding audible floor identification at elevator, including labor.
15. $2,600 each for Main Building Entry exterior sign.
16. $70 each for access route sign.
17. $1,350 each for power-assist door opener and switches, including labor.
18. $55 each for one additional grab bar in rest room.
19. $5,500 each for adding one barrier free stall in a rest room, including labor.
20. $130 each for barrier free sign on post.
21. $80 each for replacement of existing exit sign with more visible style.
22. $1,800 each for replacing drinking fountain with ADA model, including labor.
23. $42/ft. for adding ADA handrail on ramps.
24. $90 each for ADA Information Direction Sign.
25. $5.50/sf. for adding side walk at ramp areas, installed including labor.
Basis of Quotes:
1. All materials quoted are for commercial mid-grade products.
2. Quotes listed above are materials only (labor is only included where noted).
3. All quotes are budget numbers based on installing all ADA updates per building unit.
4. Individual items can not be completed one at a time at this cost.
5. 2009 prices quoted will be good for 6 months.